小弟新居目前正在裝潢
最金終於要動到魚缸了
5X2X2冷卻機效率需要多少BTU?
有沒有推薦的廠商
使用日系主機會較穩定嗎?
 
5x2x2=>>[FONT=新細明體]約[/FONT]550L[FONT=新細明體]的海水[/FONT]
[FONT=新細明體]降溫目標設為[/FONT]6[FONT=新細明體]℃[/FONT]/hr[FONT=新細明體]溫差[/FONT]([FONT=新細明體]即[/FONT]1[FONT=新細明體]小時能把[/FONT]32[FONT=新細明體]℃降到[/FONT]26[FONT=新細明體]℃[/FONT])
[FONT=新細明體]已知海水比熱[/FONT]=0.93,[FONT=新細明體]安全係數[/FONT]10%
[FONT=新細明體]目前市售冷水機[/FONT]COP[FONT=新細明體]值約[/FONT]2.0
550x6x0.93*1.1=3376kcal/hr=13396BTU//hr
=3.925 kW(1.12[FONT=新細明體]冷凍噸[/FONT])
3.925/2.0=3.925 Kw=2.63Hp[FONT=新細明體]電入力[/FONT]
[FONT=新細明體]所以壓縮機取[/FONT]3HP
 
5x2x2=>>[FONT=新細明體]約[/FONT]550L[FONT=新細明體]的海水[/FONT]
[FONT=新細明體]降溫目標設為[/FONT]6[FONT=新細明體]℃[/FONT]/hr[FONT=新細明體]溫差[/FONT]([FONT=新細明體]即[/FONT]1[FONT=新細明體]小時能把[/FONT]32[FONT=新細明體]℃降到[/FONT]26[FONT=新細明體]℃[/FONT])
[FONT=新細明體]已知海水比熱[/FONT]=0.93,[FONT=新細明體]安全係數[/FONT]10%
[FONT=新細明體]目前市售冷水機[/FONT]COP[FONT=新細明體]值約[/FONT]2.0
550x6x0.93*1.1=3376kcal/hr=13396BTU//hr
=3.925 kW(1.12[FONT=新細明體]冷凍噸[/FONT])
3.925/2.0=3.925 Kw=2.63Hp[FONT=新細明體]電入力[/FONT]
[FONT=新細明體]所以壓縮機取[/FONT]3HP

大大你忘了算底缸了
扣掉濾材 溢流 及其它空間
水量大約750公升
 
Sailor大, 我主缸尺寸跟你一模一樣!!! 目前用1.3噸室外機綽綽有餘! 有需要購買資料不用客氣, 請短訊息給我~~~
你所謂日系主機是指"變頻"的嗎? 我問過了, 沒有室內機的主機版可以搭配控溫器.... 所以都是沒有變頻的!
給您參考喔~~~ :em03::em03::em03:
 
Sailor大, 我主缸尺寸跟你一模一樣!!! 目前用1.3噸室外機綽綽有餘! 有需要購買資料不用客氣, 請短訊息給我~~~
你所謂日系主機是指"變頻"的嗎? 我問過了, 沒有室內機的主機版可以搭配控溫器.... 所以都是沒有變頻的!
給您參考喔~~~ :em03::em03::em03:
您好,我最近也要裝璜,煩請提供購買資料,萬分感謝!
 
[FONT=新細明體]"降溫目標設為[/FONT]6[FONT=新細明體]℃[/FONT]/hr[FONT=新細明體]溫差"[/FONT]
[FONT=新細明體]這裡要修正為1~2℃/hr就足夠ㄌ~[/FONT]
通常只有第一次啟動會有那麼大ㄉ溫差~
之後就只會設0.8~2℃左右的溫度差ㄌ!
所以1000L以內ㄉ總水量都可以使用10000BTU
如要大些ㄉ12000BTU也都足夠ㄌ!
不用買那麼大ㄉ室外機~耗電!
 
不過增設冷水系統 除了考量水量外還要看你的熱源(燈,擺放位置,馬達數量)
所以開燈時間不常 馬達不多的情形下 魚缸本身大致用一頓的壓縮機即可
就我看過某些水族館 即使魚缸(500L左右)放在環境溫度高的地方 也只用一頓的室外機
 
小弟10尺缸,水量約3000L
室外機是8000BTU
平常降一度約70分
1660w 燈具全開時降一度約120分
 